Using MC024 to control s20 pump
« on: September 25, 2023, 02:05:51 PM »
Hello,

Could anyone tell me if it is at all possible to use PLUS+1 software to control pumps like those from s20? Better yet, is there any way to change output current on a pin ? Let's say I use standard s90 EDC block in GUIDE and I want to get it to 100mA (while standart for EDC on s90 should be 85mA)?

Thank you all in advance.

Offline FluidPowerTom

  • PLUS+1 Guru
  • *****
  • Posts: 363
  • Karma: +33/-0
Re: Using MC024 to control s20 pump
« Reply #1 on: September 25, 2023, 05:12:46 PM »
You can control current as high as you like up to 3,000 mA on most outputs.  I'm not sure if you'd do this by changing a setting in the S90 compliance block or by just making your own code, but either way I think it'll work fine.
Controls Engineer
Hydra-Power Systems

Offline Lukey

  • PLUS+1 Expert
  • ****
  • Posts: 72
  • Karma: +8/-0
Re: Using MC024 to control s20 pump
« Reply #2 on: September 26, 2023, 06:00:01 AM »
If using the S90 EDC block then yes you can change the max current to 100mA, changes are made in the Config_data page of the compliance block.

Offline Mr.Jacobee

  • PLUS+1 Novice
  • *
  • Posts: 2
  • Karma: +0/-0
Re: Using MC024 to control s20 pump
« Reply #3 on: September 26, 2023, 08:30:08 AM »
Thank you guys very much ;)